This is with reference to section 12 (Design and detailing for earthquake loads) of the draft IS: 800, its correlation with IS: 2062 and availability of steel products.
Aseismic design heavily relies upon post-yield inelastic response of 结构,特别是SMF evident from the response reduction factor (R). It implies that if the design criteria for SMF are followed, then steel sections would be able to undergo plastic deformation at specific locations to form a predicted mechanism. Therefore, such frames are capable of collapse prevention and life safety performance, even if they are designed for relatively less seismic load.
As per IS: 2062, Fe 410W Grade-A steel is to be adopted only for non-critical applications (Refer to Foreword), where there is no risk of brittle failure. Otherwise, Grade-B steel should be used, wherever the structure is subjected to severe fluctuation of stresses.
The risk of brittle failure cannot be accepted by any means in aseismic design. This warrants usage of Grade-B steel strictly. But in reality, I understand, manufacturers (irrespective of what their catalogue shows) are producing Grade-A steel in general and Grade-B steel is not readily available. As a result, we find only Grade-A steel is used to build structures in India, except for plates having thickness > 20mm. All the structural components (except large crane girders) are of Grade-A steel, including the lateral load resisting system of the structure. So also the connections adopting plate thickness lower than 20mm. For illustration, this applies for large span trusses, columns, bracing etc.
I was just pondering over .......
1) Does not this go against the criteria of earthquake resistant design by enhancing the risk of brittle failure? Here also, the structure is subjected to severe fluctuation of stresses in the inelastic range.
2) If the above understanding is incorrect, than how the usage of Grade-A steel is justified in lateral load resisting system and the connections, in view of earthquake resistance?
My concern is, if the material of construction (as available) does not support or not compliant with design philosophy prescribed by the code, then adhering to the codal provisions will not yield the desired result.
I shall be grateful for the advice / view of learned Moderators and Participants, in this regard.