Dear sir/ Madam,
As per section 5.4.1 the lateral drift ratio (under factored wind load combinations) is given as H/500 and for single story it is given as h/400. For earthquake load (factored) combinations it is given as h/250. H=total ht of the building h=ht of one story
My question is for which unfactored wind load combinations and factored earthquake load combinations the drift value is to be considered.�
Also does H/500 states the limitation for maximum deflection of building as tatal height is considered.�
Kindly give some clarity on this clause....
Regards, Chirag Chaudhari.
Posted via Email |
|
Back to top |
|
|
alpa_sheth ...
Joined: 26 Jan 2003 Posts: 278
|
Posted: Wed Mar 14, 2018 5:27 amPost subject: Drift limitations in IS 16700 |
|
|
The use of factored/unfactored needs to be understood.�
Unfactored wind� loads are easy to understand. They are the design wind loads without any load combination factors of 1.5, 1.2 etc.� Factored� earthquake loads are also the design earthquake loads without any load combination factors of 1.5, 1.2 etc. The reason they are called "factored" loads is because you have used a response reduction factor R to factor down the earthquake force levels.
regards, A
best regards,Alpa Sheth�
VMS Consultants Pvt. Ltd. 83 Sakhar Bhavan 230 Nariman Pt.� Mumbai 400021 Tel: 91-22-61725200 w (vmsb@vakilmehtasheth.com)ww.vakilmehtasheth.com
结婚,3月14日,2018年在9:06,chiragchaudhari forum@www.buonovino.com)> wrote:
Quote: |
Dear sir/ Madam,
As per section 5.4.1 the lateral drift ratio (under factored wind load combinations) is given as H/500 and for single story it is given as h/400. For earthquake load (factored) combinations it is given as h/250. H=total ht of the building h=ht of one story
My question is for which unfactored wind load combinations and factored earthquake load combinations the drift value is to be considered.�
Also does H/500 states the limitation for maximum deflection of building as tatal height is considered.�
Kindly give some clarity on this clause....
Regards, Chirag Chaudhari.
|
Posted via Email |
|
Back to top |
|
|
hemalmistry ...
Joined: 01 Jul 2009 Posts: 70
|
Posted: Wed Mar 14, 2018 5:52 amPost subject: |
|
|
Alpa mam, Thanx for the clarification regarding "factored seismic load", as generally we mean factored load combinations are load combinations with PSF for loads applied to each load.
Regards hemal |
|
Back to top |
|
|
chiragchaudhari SEFI Member
Joined: 18 Jul 2017 Posts: 3
|
Posted: Wed Mar 14, 2018 6:53 amPost subject: Drift limitations in IS 16700 |
|
|
Thank you for making it more clear.
I have one more query. The same clause suggest the relaxation of drift limitation to h/400 for single story. What exactly it is for..??
Regards, Chirag Chaudhari
On Wed, Mar 14, 2018, 11:03 alpa_sheth forum@www.buonovino.com)> wrote:
[quote]​The use of factored/unfactored needs to be understood.�
Unfactored wind� loads are easy to understand. They are the design wind loads without any load combination factors of 1.5, 1.2 etc.� Factored� earthquake loads are also the design earthquake loads without any load combination factors of 1.5, 1.2 etc. The reason they are called "factored" loads is because you have used a response reduction factor R to factor down the earthquake force levels.
regards, A
​
best regards,Alpa Sheth�
]https://drive.google.com/uc?id=0B4BXntATUzLzTWdET1NuSmJtUTA&export=download">
VMS Consultants Pvt. Ltd. 83 Sakhar Bhavan 230 Nariman Pt.� Mumbai 400021 Tel: 91-22-61725200 w (vmsb@vakilmehtasheth.com (vmsb@vakilmehtasheth.com))ww.vakilmehtasheth.com
On Wed, Mar 14, 2018 at 9:06 AM, chiragchaudhariforum@www.buonovino.com (forum@www.buonovino.com))> wrote: --auto removed--
Posted via Email |
|
Back to top |
|
|
|
|
Youcannotpost new topics in this forum Youcannotreply to topics in this forum Youcannotedit your posts in this forum Youcannotdelete your posts in this forum Youcannotvote in polls in this forum Youcannotattach files in this forum Youcannotdownload files in this forum
|
|
|