www.www.buonovino.com

STRUCTURAL ENGINEERING FORUM OF INDIA [SEFI]

Forum SubscriptionsSubscriptionsDigestDigest PreferencesFAQFAQSearchSearchMemberlistMemberlistUsergroupsUsergroupsRegisterRegisterFAQ安全提示FAQDonate
ProfileProfileLog in to check your private messagesLog in to check your private messagesLog in to websiteLog in to websiteLog in to websiteLog in to forum
Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.

Eccentric Footing Design
Goto page1,2Next
Post new topicReply to topicThank Post www.www.buonovino.com Forum Index->SEFI General Discussion
View previous topic::View next topic
Author Message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 101

PostPosted: Wed Dec 14, 2022 4:10 pmPost subject: Eccentric Footing Design Reply with quote

Dear All,

Can we design the eccentric footing for the attached plan as per the attached calculation?

Kindly guide me on this.

Thanks & Regards,
Ramu.



Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
DESIGN OF FOOTING FOR EDGE COLUMN1.pdf
Description:

Download
Filename: DESIGN OF FOOTING FOR EDGE COLUMN1.pdf
Filesize: 146.88 KB
Downloaded: 255 Time(s)


Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
Eccentric footing-Model.pdf
Description:

Download
Filename: Eccentric footing-Model.pdf
Filesize: 123.05 KB
Downloaded: 287 Time(s)

Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Thu Dec 15, 2022 4:31 amPost subject: Reply with quote

Eccentric footing on boundary edge :

Dear Er -

First and foremost task in sbove footing is working out base pressure correctly.

You have taken uniform base pr,, You can do so in case you tie this column to some opposite interior column by a beam called Strap beam .

You may see for yourself that bade pressre Max will exceed many times, if Strap beam is not provided

But in this case : Pl see Max base pr as under -
P= Column vertical load
B = Footing size in ecc direction
L = footing size in ortho dir
d = col dim in ecc dir

Since yr col load is at edge of footing, there is eccentricity of load wrt to footing centrline.
e = (B/2 - d/2)
一刻开始基础= P * e

Footing will lift and max base pr will be very very high

Please refer sny text book for design calcs

Some relief in moment on footing due to above ecc is provided by passive soil resistance thru edge wall,, but is not much compared to ecc moment.
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Thu Dec 15, 2022 4:39 amPost subject: Reply with quote

You can refer earlier detailed discussions on Edge footings in topic " Some general view '
Back to top
View user's profileSend private message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 101

PostPosted: Thu Dec 15, 2022 9:36 amPost subject: Reply with quote

Thank you Sir.

Kindly share if you have any references to designing the eccentric footing with a strap beam.

For example,

Edge Footing

Load on column - 300 kN

SBC - 200 kN/Sqm

Column size - 200 x 450 mm

Attached is the image for your reference.

Thanks & Regards,
Ramu.



Strapbeam.png
Description:
Filesize: 14.58 KB
Viewed: 50 Time(s)

Strapbeam.png


Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Thu Dec 15, 2022 10:59 amPost subject: Reply with quote

Et Ramu,,

By connecting edge column to inner column at footing level itself thru strap beam,, the base pressure could be approx P/A ,, but strap beam has to resist eccentric moment P*e as discussed in previous post.

Reiforcement is provided at top.,, bottom bars could be nominal ones.
Approx Moment in strap beam can be taken as M=P*e with 10% reduction for soil passive relief,, but better workout passive relief from side wall in footing zone.

Shesr force - entire shear is balanced within the footing being resisted by footing concrete ,, hence stps can be nominal but pl see some text book also for better understand ing of subject.
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Fri Dec 16, 2022 2:36 pmPost subject: Reply with quote

Very old posting from respected BV Harsoda saheb wherein discussion on edge footing was there :-


B.V.Harsoda wrote:
In previous posting Er. Vikramjeet has been Explained nicety as Below:-


"L- Footings is generally required to be provided at the edge of
property line. This footing, if not connected to internal column, is
subjected to very high moment due to eccentricity of load w r t
footing centreline.
It is always preferable to connect this footing with some
我nternal column through a strap beam so that moment
due to eccentricity is taken care by this beam.For economy
我n strap beam, it is necessary to take footing dimension
我n direction of eccentricity,as less as possible,say, half the other.

"For edge footing without strap beam,it is difficult to satisfy
the no upliftment condition as redistribution is not permitted
for footings resting on soils.Even if some redistribution is
taken it may give very high value of upliftment of footing
and max pressure after redistribution is quite high(it has to be
less than SBC)
Some designers take advantage
of passive soil resistance(with some FOS) offered by the edge wall
to relieve eccentric moment but in that case edge wall shall
be strong enough to withstand this passive relief moment.

Long back I had seen a paper written by structural expert and author
Sh UH Varyani on the analysis of edge footing w/o strap
beams. This might be available in some of his books
."



In Second Post said that

"in my opinion ,try to provide strap beam as per situation
given below in view of L-footing already cast without
strap beam.

我)assuming that columns are not cast above top of footing

在这种情况下你可以提供带梁
connecting this column to internal column at
top of footing level .

我我)assuming that columns are cast above top of footing
upto GL/PL
在这种情况下你可以提供带梁(tie beam)
connecting this column to internal column at
GL/PL but edge column reinf provided shall be adequate
enough to transfer the eccentric moment upto
strap / tie beam level. You can take advantage of
passive relief from soil(with some FOS) on edge wall on
either side of column .Also the orthogonal cross wall (if it exists)
will help. ( by way of its triangular load component beyond
footing line through dispersion which will provide counter
eccentricity)"






Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Fri Dec 16, 2022 2:43 pmPost subject: Reply with quote

Earlier posting from my end :

Plinth beam at plinth level can also help , but in that case there is need to
for additional forces to be taken into consideration .

There are two alternatives - - - - -

1 ] Alternative A -- Additional forces in Column , Plinth beam as well as check
of other columns on plinth beam grid

Provide additional reinf in column for eccentric moment M. This reinf needs to
be provided from footing to plinth beam (with Ld embedment in both ), and
plinth beam need s to be designed for additional tensile force T= M/Df .
The columns on inner side with which this plinth beam is tied also to be
checked for a force T/N

Df is the foundation depth
( More precisely vertical distance from from CL of footing to CL of Plinth B)

N - - is the nos of other columns in that grid tied by plinth beam.

2 ] Alternative B- - Plinth beam designed as strap beam with filler 345thk
brick wall for light loadings/and pcc wall 1:3:6 for high loading between
footing -top and plinth -beam -underside.

This wall will be sandwiched between footing and plinth beam. This will be
subject to upward force =column load which in turn act on plinth beam
to be designed as strap beam.


best regds

vikramjeet



Dear Er vikram.jeet Sir If we provide Plinth beam instead of strap beam in case of eccentric footing so that it connects to inner column to take care of eccentric moment Please comment on this Regards
-- ��

Posted via Email
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Fri Dec 16, 2022 2:57 pmPost subject: Reply with quote

Earlier posting of 31.05.2010

vikram.jeet wrote:
Dear Er Venkatesh ji ,

14" brick walls are definitely supportive and bearing capacity of 30 tonne /sqm is
very good strata.But since the structure is old, 14" walls may need re-plastering.
Also please check the footing offset from wall by excavating(exposing) from outside.

For extension , if the walls are planned exactly over the GF walls, extension may
be carried out but it must be seen that walls must have cross walls at about
10' to 12' interval (which generally exists in a residential building).Footing
width must be checked for (new loading+existing loading).

As regards L - type footing -- These are the one sided footings with column
located at edge .
The corner footings of this type are eccentric in both the directions with column
位于角落的基础。这将要求e strap beams in both directions
The intermediate L type footings are eccentric in one direction with column located
,though at edge ,but at centre in length direction.Thse will require strap beam in
one direction only.
These footings are provided out of compulsion when
(i)column happens to be on property line and it is not possible to provide
a concentric footing.
(ii) When additions /alterations in existing structure are required -- as the case
under present discussion.

For design ,must refer any standard text book on structures design.
Unless concept is clear ,don't move ahead in design.

However as a quick design, please calculate the moment for which strap beam
to be designed as under:
Moment = P * e
P--- Column Load
e - Eccentricity ( Distance between centre line column to centre line footing in direction
of eccentricity)
Some reduction in this moment is possible due to( passive less active) relief of soil on footing
back face(and wall face if wall at back exists).

If L -footing happen to be at corner, it has to be planned as square shape
However at intermediate location, try to keep Length of footing along the property line
and L/B shall be planned >2.0 to 2.5 .This would keep the eccenricity minimal and
result in economical design of strap beam.

For such footings the column pedestal dimension on eccentric side shall be increased
to about 22.5 to 30 cm as against 15cm for generally given for normal footings

Direction of tensile reinf in strap beam-- As already discussed two situations may be posiible
(i) Edge columns on property line will have only one posiibility -- L- footings with footings
我nside the plot connected to opposite column(Concentric/eccentric).Strap beam runs
我n direction of footing Overhang and passes through it

(ii) Additions /Alterations cases: Possibility of providing revese L type footings is also
possible in addition to (i). Strap beam runs in reverse direction of footing Overhang

For (i) Tensile reinf in strap beam is needed at TOP
For (ii) Tensile reinf in strap beam is needed at BOTTOM

Shear reinf in strap beams is nominal as entire shear is generally balanced by footing
over hang and it is a case of more or less uniform moment (approx no shear)


regards

vikramjeet

Posted via Email
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3699

PostPosted: Sat Dec 17, 2022 3:50 pmPost subject: Reply with quote

Situation now a days reg L footings :

In big projects with proper supervision , whatever detais a str engineer give in drg ,, are followed without if / but.

But in projects where client is ignorant ,, no / poor supervision ,, that too by non Civil er ,, there are possibilities that Strap beams are not provided , and unless supervised ,, no body knows , Missing is due to fact that additional excavaton for strap beam right upto found lvl. Even many site ers have tendency to ignore here.
However in present times with what's app facility photos must be demanded by Str Consultant when reinf is placed and strap beam ,provided/ not can be easily seen distantly .
Back to top
View user's profileSend private message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 101

PostPosted: Tue Dec 20, 2022 6:10 amPost subject: Reply with quote

Thank you, Sir.

I will resolve one problem and update you.
Back to top
View user's profileSend private message
Display posts from previous:
Post new topicReply to topicThank Post www.www.buonovino.com Forum Index->SEFI General Discussion All times are GMT
Goto page1,2Next
Page1of2



Jump to:
Youcannotpost new topics in this forum
Youcannotreply to topics in this forum
Youcannotedit your posts in this forum
Youcannotdelete your posts in this forum
Youcannotvote in polls in this forum
Youcannotattach files in this forum
Youcandownload files in this forum


© 2003, 2008 SEFINDIA,Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service.advertisement policy
Baidu
map