akuc007 SEFI Member
Joined: 25 Aug 2015 Posts: 14
|
Posted: Mon Dec 05, 2022 11:10 amPost subject: wind load calculation BS 6399-2 1997 |
|
|
Hi all, As i am in calculation of Wind load for 20m tall building based on BS 6399-2 (due to project requirement). However the project (location Qatar) spec provided the basic wind speed @ 3 sec gust wind speed.
Since the code is using Mean hourly wind speed as basic wind speed, i have to change the V(3sec-gust = 50 m/s)) to V(hourly mean =32.55 m/s) with (dividing) terrain and building factor Sb (table-4 [sb = 1.536] [conversion method given in forward]).
However to calculate the effective wind speed (to arrive dynamic pressure) again i have to multiply with Sb factor make V effective Ve = 50.75m/s (decimal changes due to Sd,Sp,Sa, Ss factor).
Where am i missing the influence of height of building.
regards Arunkumar. |
|
Back to top |
|
|
vikram.jeet General Sponsor
Joined: 26 Jan 2003 帖子:3699
|
Posted: Sun Dec 11, 2022 10:45 amPost subject: |
|
|
Not seen BS 6399-2
Wind loads Code IS 875part 3 take terrain height factor for working out wind speed at its table 2 ,, (coeff k2).
For Tall buildings , Gust factor Method as given at cl 10.2 &10.3 are there in IS. Our Codes are revised based on research here as well as Internationally.
I Think if u follow IS code steps / procedure , some revelation of ht may be revealed to you while following BS parallely.
I am really sorry not to help in this aspect. |
|
Back to top |
|
|
akuc007 SEFI Member
Joined: 25 Aug 2015 Posts: 14
|
Posted: Sun Dec 11, 2022 3:12 pmPost subject: |
|
|
Thanks for your reply Mr. Vikram.
however i have to use the BS code as project requirement. lets wait for some light on this by somebody.
The structures in the project are <15m so no much effect will be in reality. however i wonder where i loss of height effect during conversion.
vikram.jeet wrote: |
Not seen BS 6399-2
Wind loads Code IS 875part 3 take terrain height factor for working out wind speed at its table 2 ,, (coeff k2).
For Tall buildings , Gust factor Method as given at cl 10.2 &10.3 are there in IS. Our Codes are revised based on research here as well as Internationally.
I Think if u follow IS code steps / procedure , some revelation of ht may be revealed to you while following BS parallely.
I am really sorry not to help in this aspect. |
|
|
Back to top |
|
|
|
|