www.www.buonovino.com

STRUCTURAL ENGINEERING FORUM OF INDIA [SEFI]

Forum SubscriptionsSubscriptionsDigestDigest PreferencesFAQFAQSearchSearchMemberlistMemberlistUsergroupsUsergroupsRegisterRegisterFAQ安全提示FAQDonate
ProfileProfileLog in to check your private messagesLog in to check your private messagesLog in to websiteLog in to websiteLog in to websiteLog in to forum
Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.

FLOATING COLUMN

Post new topicReply to topicThank Post www.www.buonovino.com Forum Index->SEFI General Discussion
View previous topic::View next topic
Author Message
devenderkumarsuthar
SEFI Member
SEFI Member


Joined: 24 Aug 2021
Posts: 1

PostPosted: Thu Sep 29, 2022 5:29 amPost subject: FLOATING COLUMN Reply with quote

SIR/MAM

我有QUAERY浮动列。是什么CORRECT PROCESURE FOR DESIGNING OF FLOATING COLUMN IS WE HAVE TO TAKE REACTIONAT THE END BUT USING PINNED SUPPORT. AND THEN WE HAVE TO DESIGN BEAM FOR THAT REACTION AND FURTHER REMOVLE THE PINNED SUPPORT AND DESIGN THE FLOATING COLUMN.
IS THIS IS THE RIGHT PROCESURE.
OR WE HAVE TO DIRECTLY DESIGN IN SOFTWARE.
IS FLOATING COLUMN IS ALSO DESIDNED FOR EARTHQUAKE LOAD
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
帖子:3699

PostPosted: Thu Sep 29, 2022 6:51 amPost subject: Reply with quote

Floating columns


Floating Columns , Concealed Beams , Thin Columns (150 wide ) are unconventional Structural elements being provided by some bold Structural Designers out of Architectural needs and not as luxury in small constructions .

As regards Floating Columns, these do not start from foundation level but may start at certain floor over RCC beams / masonry for one or at the most two storeys but there is need to have beams at base as well as top of F/cols at each floor level . Beams , if provided in both directions , is better .
In design , the F/ Columns are treated as pinned base for Gravity loading . The earthquake forces for loading shared by these Columns need to be transfered to main building Columns in manual working , but these F Columns need to be designed for at least 25% of EQ , though 100% of their EQ is transferred to Main Columns. Modelling needs to be done accordingly.

Also Please refer IS 1893 in regard to Gravity Columns which are not Floating Columns, but Columns in rcc construction taking care of gravity loading only. Floating column at floor where provided can be treated similarly for EQ .
Back to top
View user's profileSend private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
帖子:3699

PostPosted: Fri Sep 30, 2022 2:51 amPost subject: Reply with quote

FLOATING COLUMNS :

Even in Buidings like 5 star Hotels , Floating Columns are provided from first floor upwards , but floating columns emerge up from a heavy TRANFER GIRDER resting (monolithic ) to Large RCC columns at ground storey , ( GF generally of double height with huge entrance canopy and big hall ) .

Transfer Girder is designed for Gravity loading and moments under Normal condition and under EQ case it is to be designed for flexural / and twisting moments due to base shear from floating columns. In this case floating columns going up are not gravity columns but also share full EQ and pass on base shear to TG.

However in case of shear walls taking care of EQ forces of building , the floating columns can also be treated as gravity columns.
Back to top
View user's profileSend private message
Display posts from previous:
Post new topicReply to topicThank Post www.www.buonovino.com Forum Index->SEFI General Discussion All times are GMT
Page1of1



Jump to:
Youcannotpost new topics in this forum
Youcannotreply to topics in this forum
Youcannotedit your posts in this forum
Youcannotdelete your posts in this forum
Youcannotvote in polls in this forum
Youcannotattach files in this forum
Youcandownload files in this forum


© 2003, 2008 SEFINDIA,Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service.advertisement policy
Baidu
map